Default bolted splice

Hi Tony

looking at the calculations for bolted splices it works out the moment capacity at the splice both in bending and shear and gives the maximum moment and shear in bold type

However it does not flag that that the moment capacity could be less than the actual moment at the splice and does not seem to flag a fail if the capacity is less than the actual

The actual moment at the splice is in normal type at the start of the calculation so you always need to check the moment capacity is greater than the actual

In eurobeam it seems top flag a fail I think


motorphotos is offline   Reply With Quote
Old 19th February 2018, 11:20 AM   #2
Tony Bryer
Join Date: Apr 2008
Location: Melbourne, Australia
Posts: 795
Default Re: bolted splice

Apologies for the late reply. This has been flagged and will be fixed in the next release. In the meantime all users should take care to check that the splice moment capacity is equal to or greater than the design moment at the splice position.
Tony Bryer, Greentram Software Pty Ltd
Tony Bryer is offline   Reply With Quote

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

All times are GMT. The time now is 01:52 PM.

Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.
Copyright 2011 Greentram Software Pty Ltd, Melbourne, Australia