Default Spread of point load in wall

Hi, I am working out the load on an existing foundation in a bungalow.

I know the weight of the wall and floor etc which are on the foundation but my problem is with the point load from a steel beam which I have designed with Superbeam.

How is the point load dispersed or spread through the wall. For example if the point load is 17.5KN and the wall is 3.6m high from top of concrete to top wall/beam position, what would the loading be for the worst 1m of foundation directly beneath the point load?
Nigel Lewis is offline  
Old 12th April 2010, 06:15 PM   #2
Tony Bryer
Administrator
 
Join Date: Apr 2008
Location: Melbourne, Australia
Posts: 780
Default Re: Spread of point load in wall

The general rule, assuming that the layout allows it, is to assume that a concentrated load spreads out as a equilateral triangle below the load, so in your case the load ends up being spread over a 3.6m length of foundation. If there are openings or the load is applied near the end of a wall then this assumption will need to be modified accordingly.
__________________
Tony Bryer, Greentram Software Pty Ltd
Tony Bryer is offline  
Old 14th April 2010, 08:26 AM   #3
John Cranna
Senior Member
 
Join Date: Jul 2008
Posts: 33
Default Re: Spread of point load in wall

I have always taken a 45 degree spread from a point load down the wall and thus if the load is 3.6 m up from the footing then it wil spread over a length of 7.2m (3.6 m each side). I would be interested to see if other people go by this or by Tony's principle.

John Cranna
John Cranna is offline  
Old 14th April 2010, 09:10 AM   #4
Tony Bryer
Administrator
 
Join Date: Apr 2008
Location: Melbourne, Australia
Posts: 780
Default Re: Spread of point load in wall

Yes, on reflection I have assumed 45 degrees in the past. The 60 degree (equilateral triangle) figure comes from Eurocode 6 EN-1996-3 4.3.
__________________
Tony Bryer, Greentram Software Pty Ltd
Tony Bryer is offline  
Old 22nd March 2011, 08:18 AM   #5
sadmemories20
Member
 
Join Date: Mar 2011
Posts: 1
Default Re: Spread of point load in wall

I know the weight of the wall and floor etc which are on the foundation but my problem is with the point load from a steel beam which I have designed with Superbeam.

Last edited by Tony Bryer; 22nd March 2011 at 11:15 AM. Reason: Non-relevant link removed
sadmemories20 is offline  
Old 22nd March 2011, 11:17 AM   #6
Tony Bryer
Administrator
 
Join Date: Apr 2008
Location: Melbourne, Australia
Posts: 780
Default Re: Spread of point load in wall

Quote:
Originally Posted by sadmemories20 View Post
I know the weight of the wall and floor etc which are on the foundation but my problem is with the point load from a steel beam which I have designed with Superbeam.
I don't wish to sound unhelpful, but if you are going to use any of our programs for real-life projects you do need to be able to accurately assess the loads on members and understand how these are entered in the program being used.
__________________
Tony Bryer, Greentram Software Pty Ltd
Tony Bryer is offline  
Closed Thread

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off



All times are GMT. The time now is 03:43 AM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright 2011 Greentram Software Pty Ltd, Melbourne, Australia